The R-134a refrigeration unit of a food-service walk-in cooler, shown in the figure, operates on a vapor-compression cycle. Refrigerant leaves the evaporator as saturated vapor at 10°F (state 1) and leaves the condenser as saturated liquid at 100°F (state 3). The expansion valve is adiabatic. A test shows that the refrigerant leaves the compressor with an enthalpy of 120.4 Btu/lbm (state 2). Using the Handbook's R-134a saturation table, the coefficient of performance of the refrigerator is most nearly:
Swipe the diagram sideways to see all of it.
- A3.77
- B4.77
- C5.22
- D5.66
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerA3.77
Find it in the Handbook
Thermodynamics
COMMON THERMODYNAMIC CYCLES
Refrigeration cycle, with across the expansion valve; saturated enthalpies from the R-134a table
Search (Ctrl+F)
Given
- State 1: saturated vapor at 10°F (evaporator exit)
- State 2: compressor exit, Btu/lbm
- State 3: saturated liquid at 100°F (condenser exit); adiabatic expansion valve
Find
Coefficient of performance
Table enthalpies
R-134a table: at 10°F Btu/lbm; at 100°F Btu/lbm. The valve is a throttle, so Btu/lbm.
COP
.
Why the other choices are wrong
- B4.77 is the heat pump COP, . For a refrigerator the useful effect is the heat absorbed in the evaporator, Btu/lbm.
- C5.22 is the reversed-Carnot COP, . That is the upper limit for any refrigerator between these temperatures; this cycle's COP comes from its enthalpies.
- D5.66 comes from taking as saturated liquid at the evaporator temperature, 15.328 Btu/lbm. The throttling valve keeps the enthalpy constant, so Btu/lbm, the liquid enthalpy at 100°F.
Exam-day tip
In refrigeration cycles, the enthalpy entering the evaporator equals the enthalpy leaving the condenser, because the valve is a throttle. Read at the condenser temperature, never at the evaporator temperature.