Refrigeration and heat pump cycles

Refrigeration and heat pump cycles is one of the subtopics of Thermodynamics in the FE Mechanical exam specification. Questions here are short: one scenario, four choices and about three minutes to answer with the FE Reference Handbook open beside you.

What you can be asked

These are the ideas our problems on Refrigeration and heat pump cycles are built around. Each one is covered by at least one problem in the bank.

  • Vapor-compression COP
  • Refrigeration capacity and tons
  • Heat pump COP
  • Reversed Carnot COP
  • Refrigerant mass flow rate
  • Compressor power from the P-h diagram

Our practice bank has 6 problems on refrigeration and heat pump cycles. Every problem is a calculation with a numeric answer. 1 of them come with a diagram. 3 use SI units and 3 use US customary units, as the exam mixes both.

Try one: a free Refrigeration and heat pump cycles problem

The solution shows the steps with units, where the equation sits in the Handbook, and the mistake behind each wrong choice.

Free sample US customary units

The R-134a refrigeration unit of a food-service walk-in cooler, shown in the figure, operates on a vapor-compression cycle. Refrigerant leaves the evaporator as saturated vapor at 10°F (state 1) and leaves the condenser as saturated liquid at 100°F (state 3). The expansion valve is adiabatic. A test shows that the refrigerant leaves the compressor with an enthalpy of 120.4 Btu/lbm (state 2). Using the Handbook's R-134a saturation table, the coefficient of performance of the refrigerator is most nearly:

Swipe the diagram sideways to see all of it.

Condenser, 100°FHeat outEvaporator, 10°FHeat inCompressorWork in12Expansion valve34
  1. A3.77
  2. B4.77
  3. C5.22
  4. D5.66

Work it out first. On the exam you would have about three minutes.

Show the answer and worked solution

AnswerA3.77

Find it in the Handbook

Thermodynamics

COMMON THERMODYNAMIC CYCLES

Refrigeration cycle, with across the expansion valve; saturated enthalpies from the R-134a table

Search (Ctrl+F)

Refrigerant 134a (1,1,1,2-Tetrafluoroethane)Coefficient of PerformanceThrottling Valves and Throttling ProcessesCOMMON THERMODYNAMIC CYCLES

Given

  • State 1: saturated vapor at 10°F (evaporator exit)
  • State 2: compressor exit, Btu/lbm
  • State 3: saturated liquid at 100°F (condenser exit); adiabatic expansion valve

Find

Coefficient of performance

  1. Table enthalpies

    R-134a table: at 10°F Btu/lbm; at 100°F Btu/lbm. The valve is a throttle, so Btu/lbm.

  2. COP

    .

Why the other choices are wrong

  • B4.77 is the heat pump COP, . For a refrigerator the useful effect is the heat absorbed in the evaporator, Btu/lbm.
  • C5.22 is the reversed-Carnot COP, . That is the upper limit for any refrigerator between these temperatures; this cycle's COP comes from its enthalpies.
  • D5.66 comes from taking as saturated liquid at the evaporator temperature, 15.328 Btu/lbm. The throttling valve keeps the enthalpy constant, so Btu/lbm, the liquid enthalpy at 100°F.

Exam-day tip

In refrigeration cycles, the enthalpy entering the evaporator equals the enthalpy leaving the condenser, because the valve is a throttle. Read at the condenser temperature, never at the evaporator temperature.

Practice more Refrigeration and heat pump cycles

The bank has 6 problems on this subtopic and 60 across Thermodynamics. Practice quizzes are part of membership. Not a member yet? The free diagnostic shows which areas to work on first. Through December 31, practice quizzes are free with a free account.

More in Thermodynamics