A hot-water coil in a makeup-air unit heats outdoor air with no moisture added, as shown in the figure. Air enters the coil at 40°F at a rate of 2,000 ft³/min measured at the coil inlet, where the enthalpy is 13.9 Btu/lbm dry air and the humid specific volume is 12.7 ft³/lbm dry air. Air leaves at 95°F, where the enthalpy is 27.2 Btu/lbm dry air and the humid specific volume is 14.1 ft³/lbm dry air. The rate of heat transfer to the air (Btu/h) is most nearly:
Swipe the diagram sideways to see all of it.
- A2,090
- B113,000
- C120,000
- D126,000
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerD126,000
Find it in the Handbook
Mechanical Engineering
Pure Heating and Cooling
HVAC pure heating and cooling,
Search (Ctrl+F)
Given
- ft³/min at the coil inlet, ft³/lbm dry air
- Btu/lbm dry air at 40°F; Btu/lbm dry air at 95°F
- ft³/lbm dry air (outlet); no moisture added
Find
Heating rate
Dry-air mass flow
lbm/min lbm/h, using the inlet specific volume because the flow was measured at the inlet.
Heating rate
Btu/h, closest to 126,000.
Why the other choices are wrong
- A2,090 is the heating rate in Btu per minute, . The mass flow came out per minute; multiply by 60 min/h to get 125,669 Btu/h.
- B113,000 Btu/h comes from using the outlet specific volume: lbm/h, and . The 2,000 ft³/min was measured at the inlet, so divide by the inlet value, 12.7 ft³/lbm.
- C120,000 Btu/h comes from assuming standard air density, 0.075 lbm/ft³: . The stem gives the actual inlet specific volume; use lbm/min.
Exam-day tip
Convert a fan or coil volume flow to dry-air mass flow with the specific volume at the point where the volume flow was measured. Then every HVAC energy balance is mass flow of dry air times an enthalpy change per pound of dry air.