Heating, ventilation, and air-conditioning (HVAC) processes

Heating, ventilation, and air-conditioning (HVAC) processes is one of the subtopics of Thermodynamics in the FE Mechanical exam specification. Questions here are short: one scenario, four choices and about three minutes to answer with the FE Reference Handbook open beside you.

What you can be asked

These are the ideas our problems on Heating, ventilation, and air-conditioning (HVAC) processes are built around. Each one is covered by at least one problem in the bank.

  • Sensible heating or cooling load
  • Cooling and dehumidification
  • Adiabatic mixing of air streams
  • Evaporative cooling

Our practice bank has 4 problems on heating, ventilation, and air-conditioning (HVAC) processes. Every problem is a calculation with a numeric answer. Every problem comes with a diagram. 2 use SI units and 2 use US customary units, as the exam mixes both.

Try one: a free Heating, ventilation, and air-conditioning (HVAC) processes problem

The solution shows the steps with units, where the equation sits in the Handbook, and the mistake behind each wrong choice.

Free sample US customary units

A hot-water coil in a makeup-air unit heats outdoor air with no moisture added, as shown in the figure. Air enters the coil at 40°F at a rate of 2,000 ft³/min measured at the coil inlet, where the enthalpy is 13.9 Btu/lbm dry air and the humid specific volume is 12.7 ft³/lbm dry air. Air leaves at 95°F, where the enthalpy is 27.2 Btu/lbm dry air and the humid specific volume is 14.1 ft³/lbm dry air. The rate of heat transfer to the air (Btu/h) is most nearly:

Swipe the diagram sideways to see all of it.

Heating coilQ in140°F, 2,000 ft³/min295°FNot to scale
  1. A2,090
  2. B113,000
  3. C120,000
  4. D126,000

Work it out first. On the exam you would have about three minutes.

Show the answer and worked solution

AnswerD126,000

Find it in the Handbook

Mechanical Engineering

Pure Heating and Cooling

HVAC pure heating and cooling,

Search (Ctrl+F)

Pure Heating and Coolingmass flow rate of dry air

Given

  • ft³/min at the coil inlet, ft³/lbm dry air
  • Btu/lbm dry air at 40°F; Btu/lbm dry air at 95°F
  • ft³/lbm dry air (outlet); no moisture added

Find

Heating rate

  1. Dry-air mass flow

    lbm/min lbm/h, using the inlet specific volume because the flow was measured at the inlet.

  2. Heating rate

    Btu/h, closest to 126,000.

Why the other choices are wrong

  • A2,090 is the heating rate in Btu per minute, . The mass flow came out per minute; multiply by 60 min/h to get 125,669 Btu/h.
  • B113,000 Btu/h comes from using the outlet specific volume: lbm/h, and . The 2,000 ft³/min was measured at the inlet, so divide by the inlet value, 12.7 ft³/lbm.
  • C120,000 Btu/h comes from assuming standard air density, 0.075 lbm/ft³: . The stem gives the actual inlet specific volume; use lbm/min.

Exam-day tip

Convert a fan or coil volume flow to dry-air mass flow with the specific volume at the point where the volume flow was measured. Then every HVAC energy balance is mass flow of dry air times an enthalpy change per pound of dry air.

Practice more Heating, ventilation, and air-conditioning (HVAC) processes

The bank has 4 problems on this subtopic and 60 across Thermodynamics. Practice quizzes are part of membership. Not a member yet? The free diagnostic shows which areas to work on first. Through December 31, practice quizzes are free with a free account.

More in Thermodynamics