Free sample SI units
Humid exhaust air leaves a textile dryer at 45°C and 50 percent relative humidity. The total pressure in the exhaust duct is 101.3 kPa. Using the Handbook's steam tables for the saturation pressure, the humidity ratio of the exhaust air (grams of water vapor per kilogram of dry air) is most nearly:
- A29.5
- B30.9
- C49.7
- D65.1
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerB30.9
Find it in the Handbook
Thermodynamics
Psychrometrics
Specific humidity (humidity ratio) , with and from the saturated water temperature table
Search (Ctrl+F)
Given
- Dry-bulb °C, relative humidity
- Total pressure kPa
Find
Humidity ratio (g water vapor per kg dry air)
Vapor partial pressure
From the saturated water temperature table at 45°C, kPa. Then kPa.
Humidity ratio
kg/kg g/kg, closest to 30.9.
Why the other choices are wrong
- A29.5 g/kg comes from dividing by the total pressure instead of the dry-air pressure: . The formula uses kPa in the denominator, which gives 30.9 g/kg.
- C49.7 g/kg comes from leaving out the factor 0.622: . That ratio is moles of vapor per mole of dry air; multiply by to get mass per mass, 30.9 g/kg.
- D65.1 g/kg comes from using the saturation pressure 9.593 kPa as , which is the humidity ratio of saturated air. At 50% relative humidity, kPa, giving 30.9 g/kg.
Exam-day tip
The denominator of the humidity-ratio formula is the dry-air partial pressure, , not the total pressure. At room conditions the difference is small, but in hot, humid air it moves the answer by several percent.