A steel tension member is bolted at its ends. Its gross area is 5.00 in², its net area through the bolt holes is 4.25 in², and the shear lag factor for the connection is 0.80. The steel has a yield stress of 36 ksi and a tensile strength of 58 ksi. Use LRFD resistance factors of 0.90 for tensile yielding on the gross section and 0.75 for tensile rupture on the effective net section. Considering only these two limit states (block shear and bolt strength do not control), the design tensile strength of the member (kips) is most nearly:
- A148
- B162
- C185
- D197
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerA148
Find it in the Handbook
Civil Engineering
Limit States and Available Strengths
Tension member limit states: yielding, with , and rupture, with and ; the smaller governs
Search (Ctrl+F)
Given
- , ,
- ksi, ksi
- (yielding), (rupture)
Find
Design tensile strength, the smaller of the two limit states
Yielding on the gross section
Yielding along the member length is checked on the gross area: kips.
Effective net area
At the connection, holes remove area and shear lag keeps part of the section from being fully stressed. The effective net area is .
Rupture on the effective net section
kips.
The smaller value governs
The member fails by whichever limit state is reached first. Rupture (147.9 kips) is less than yielding (162.0 kips), so the design tensile strength is about kips.
Why the other choices are wrong
- B162 kips is the yielding strength, kips. The number is right but it is not the design strength: the rupture strength, kips, is smaller, and the smaller limit state governs.
- C185 kips comes from using the net area without the shear lag factor: kips. Rupture is checked on the effective net area, in², which gives 147.9 kips.
- D197 kips is the nominal rupture strength, kips, with no resistance factor. A design strength is : multiply by to get 147.9 kips.
Exam-day tip
Always compute both yielding and rupture and take the smaller. Yielding uses the gross area with 0.90; rupture uses the effective net area with 0.75.