Free sample US customary units
A wide-flange steel column is 18 ft long and is pinned at both ends so that it is free to buckle about either principal axis, with an effective length factor of 1.0 for both axes and no intermediate bracing. The cross-section has moments of inertia of 272 in⁴ about its strong axis and 93.4 in⁴ about its weak axis, and the modulus of elasticity is 29,000 ksi. Assuming the column is perfectly straight, concentrically loaded and remains elastic, the Euler critical buckling load (kips) is most nearly:
- A143
- B573
- C1,670
- D2,290
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerB573
Find it in the Handbook
Mechanics of Materials
Columns
Euler's Formula, , with the weak-axis
Search (Ctrl+F)
Given
- ft, pinned at both ends, about both axes
- ,
- ksi
Find
Euler critical load,
Effective length in inches
With in ksi and in , the length must be in inches: in.
Pick the axis that buckles first
The effective length is the same about both axes, so the column buckles about the axis with the smaller moment of inertia. That is the weak axis: .
Apply Euler's formula
kips.
Why the other choices are wrong
- A143 kips comes from using , the value for a column fixed at the base and free at the top. That doubles to 432 in. and divides the load by 4: kips. This column is pinned at both ends, so and in.
- C1,670 kips comes from using the strong-axis moment of inertia: kips. With the same effective length about both axes, the column buckles about the weak axis first, so use in⁴, which gives 573 kips.
- D2,290 kips comes from using , the value for a column fixed at both ends. That halves to 108 in. and multiplies the load by 4: kips. This column is pinned at both ends, so and in.
Exam-day tip
Unless bracing differs between the axes, Euler buckling always uses the smallest moment of inertia. Convert feet to inches before squaring the length.