A pressure transmitter on a compressor discharge line sends a 4 to 20 mA signal that varies linearly from 4 mA at 0 kPa to 20 mA at 1,000 kPa (gauge). The loop current passes through a 250 Ω resistor, and a data logger reads 3.10 V across that resistor. The discharge pressure (kPa, gauge) is most nearly:
- A420
- B525
- C620
- D775
Work it out first. On the exam you would have about three minutes.
Show the answer and worked solutionHide the answer and worked solution
AnswerB525
Find it in the Handbook
Electrical and Computer Engineering
Resistivity
Ohm's law, (Handbook); the linear 4 to 20 mA scaling between the calibration points in the stem (given in the stem; the Handbook has no formula for it)
Search (Ctrl+F)
Given
- Signal 4 mA at 0 kPa to 20 mA at 1,000 kPa, linear
- Sense resistor Ω, measured voltage V
Find
Discharge pressure (kPa gauge)
Loop current
Ohm's law: A mA.
Scale to pressure
kPa.
Why the other choices are wrong
- A420 kPa subtracts the 4 mA live zero but divides by 20 mA instead of the 16 mA span: . The full range corresponds to only 16 mA (4 to 20), so kPa.
- C620 kPa ignores the 4 mA live zero, treating 0 to 20 mA as the range: . The signal is 4 mA at 0 kPa, so subtract 4 mA first and divide by the 16 mA span: 525 kPa.
- D775 kPa divides the whole current by the span, , without first subtracting the 4 mA live zero. Use kPa.
Exam-day tip
For any 4 to 20 mA signal, convert to fraction of span first, with in mA. It also flags an impossible reading below 4 mA, which usually means a wiring fault.